I recently helped someone get a roto damper going and thought it would be a good idea to post the info here in the roto damper thread as well....
In the Heater Meter Config, for Servo Pulse Duration settings.... If you set the low number too low, or the high number too high, it will try to make the servo go beyond it's operational range and it can do all kinds of crazy things like, jam, vibrate, even melt! I don't know what the exact limits are on the servo off hand, but somewhere in the middle of the range is the best way to go.
So take my advice if you want this to go easy...
Separate the body of the roto damper from the barrel
Set the Servo Pulse Duration on your Heater Meter Config page to 800 - 2400 with Inverted Output
Make your Heater Meter go to 100% blower/servo output
NOW mate the body and barrel so the moon shaped openings sit directly on top of each other.
Then make the HM go to 0%, it should close completely. Then make the HM go back to 100%, it should open completely. If you are not getting complete open/close tweak your Servo Pulse Duration numbers SLIGHTLY until you do. The easiest way to tweak the settings is put your HM into the position that is not proper, then alter the number in the Config little by little until it is proper. When you save the config you should see the servo move just a little, if it doesn't move then you probably altered the wrong number....
As for the CAT5 jack wiring....
The HMv4.1.X has the rj45 on board, so the standard HM RJ45 wiring has been defined since then. It is shown on the v4.1 schematic.
Here is a pic of that part of the schematic:
Included in this pic is also the blower driver section, which I posted in the thread about how I converted my HMv4.0 blower driver circuit over to the blower driver used on the HMv4.1 and later. Reason being, V4.0 driver pulsed the ground rather than the positive lead on the blower, so the servo and blower can not share the same ground with that blower driver circuit, so the RJ45 on a HMv4.0 cannot be wired exactly like the above standard. The HMv4.1X driver pulses the positive leg of the blower and uses a regular ground and so the blower can share a ground with the servo as shown above.
If you run a HMv4.0 or older you must dedicate an extra wire for the +12v for the blower. I edited the above image to include an example of what you might use for the HMv4.0 and older and probes:
Everything that is not on the end of a green lead in the diagram is somewhat subjective, but it's a good idea to run the pit probe on the same twisted pair as the probe ground rather in the same twisted pair as the power leads or something that is pulsed like the blower or servo signal leads to prevent instability in the pit probe.
If you want to make your HMv4.0 or older run the standard HM RJ45 wiring (so you can use your damper devices on both HMv4.0 and 4.1 units) you would have to convert your HMv4.0 blower driver circuit over to the new HM4.1 style like I detailed in
this thread. It was cheap and easy for me to do and has been working great for me. This was important to me cause I work with all kinds of dampers and wanted them to all to run the standard HM RJ45 wiring. If you have a one-off HMv4.0 and a single damper, and are happy with having just the pit probe and one food probe in the CAT5 cable then you could just run the HMv4.0 wiring shown above or something similar....